Feeder tap and voltage drop?
Isaiah
Baton Rouge
Electrical Inspector
Construction ran a feeder, 600V TC cable XHHW-2 3/C #2/0 w/Grd, 550 feet to a junction box where it splits and goes in 2 directions using a larger cable, (that is #4/0’s) for about 125’ in both directions - each terminates at a 3ph 480V heater of about 50A each. How would I calculate the voltage drop for this circuit?
There will be an issue with the tap rules unless the 4/0s are outside, except for the connection to the load, and if inside that would have to be "nearest the point of entrance" of the tap conductors.
Don everything is outside
The OP is using "feeder tap" not in the 240.21 sense but in the "tee junction" sense. Two 50A loads on a combination of 2/0 and 4/0.
Cheers, Wayne
Yes it would be better described as a T