Feeder Tap Grounding conductor size
ekbrunn
I have a 350 kcmil tap connected to a bus protected by an 800 amp circuit breaker. The 350's terminate in a 200 amp circuit breaker less than 25 feet away. I feel the grounding conductor should be a minimum 1/0 per 2002 NEC Table 250.122. Am I correct?
The argument presented is that the 200 amp circuit breaker down stream of the tap only requires that a #6 be provided along with the 350 kcmil conductors. (We agree that from the 200 CB downstream a #6 is appropriate.) My argument is that equipment ground for the tap is to be sized per the OCPD ahead of the tapped feeder.
Re: Feeder Tap Grounding conductor size
You would size it per the 800 amp device upstream via Table 250.122. If there is a ground fault, the downstream device will never even see the fault.
I agree with Eprice. ;)
Roger
I agree with everyone.
Hey, I could go into politics!
NOT! :p