Feeder tap on parallel conductors

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Wondering if the attached image is okay to do?

Or do I have to tap on to each parallel phase conductor?
59741373e6be9e362209deacdc0210dd.jpg


Sent from my SM-G998U using Tapatalk
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Tap both to say a 3 port polaris tap, then a single conductor into my solar lug?

Sent from my SM-G998U using Tapatalk
Yes. Change the two port Polaris blocks to three port blocks and run all your conductors into them.
 
Yes. Change the two port Polaris blocks to three port blocks and run all your conductors into them.
I assume those are equipment lugs not Polaris connectors in the sketch, so I would use a three port Polaris block sized so the two can pass thru unsoliced to the equipment, then use the third port for the solar. Another option we would be to replace the equipment lugs with three port, but that might be tricky to find suitable lugs for that.
 