The residence is being supplied by a utility pole mounted transformer (120/240V single phase on the secondary side). The 100A underground conductors from the transformer feed the existing 100A meter socket on the house and the meter socket feeds a 100A panel with a 2 pole 100A main breaker.
In order to "move" (as requested by owner) a 100A meter on the side of a home to the utility pole wherer the transformer is located, The Power Utility is requiring that the existing components on the transformer secondary to a new meter socket be upgraded to 200A and the new pole mounted meter socket be a 200A rated meter socket with a 200 A, 2 pole circuit breaker.
As stated the existing underground conductors from the pole to the house are rated for 100A.
Are the existing underground conductors considered to be feeder taps and therefore allowed under NEC 240.21 (B)?
Is the new 200A circuit breaker considered to be a service disconnect and therefore the ampere ratings of the existing underground feeders from the 200A CB to the 100A CB at the house panel considered protected?
Thanks for input
In order to "move" (as requested by owner) a 100A meter on the side of a home to the utility pole wherer the transformer is located, The Power Utility is requiring that the existing components on the transformer secondary to a new meter socket be upgraded to 200A and the new pole mounted meter socket be a 200A rated meter socket with a 200 A, 2 pole circuit breaker.
As stated the existing underground conductors from the pole to the house are rated for 100A.
Are the existing underground conductors considered to be feeder taps and therefore allowed under NEC 240.21 (B)?
Is the new 200A circuit breaker considered to be a service disconnect and therefore the ampere ratings of the existing underground feeders from the 200A CB to the 100A CB at the house panel considered protected?