CaliforniaMike
Member
All,
I used to be an EE, many years ago, so I just got pulled into a review of an old (>70 year) oven on our production floor. I have not looked at the NEC since about 2005 so I am more than rusty. I would appreciate it if I could get a quick reality check.
The oven is supplied with 3 phase 240 by a 150 amp breaker about 25 feet away and power is landed on an abandoned 3 phase contactor with what looks to be 50 year old 2/0. From here, there are many (>10) small gauge (18-12 AWG) wires all smashed together to land on another terminal on each of the poles of the contactor terminals on the same side of the contactor as the landing. (The switched side is abandoned.) These wires then run through the oven, under the heated zone, to another panel with breakers. The entire length of these wires is enclosed in the oven, but not protected in any other way. All of the cloth insulation is fraying. The interpretation seems to be that these wires are taps.
We have an oven in house, but it may take a week or more to get ready to replace the older oven.
I have visions of 36 kW finding a way home through 18 AWG conductors so my instinct was to simply shut down the older oven until the new oven is ready to power up.
Barring this, my basic suggestions were that:
1) While we probably comply with the disconnect requirements, it would take someone that was not familiar with the oven several minutes to find it and we should just put one on the oven at the point of power entry. Short term, we should at least train everyone that works on the floor on the location of the disconnect.
2) If we wanted to run the existing oven, the wires from the 2/0 needed to directly land on some kind of distribution board and directly feed breakers, not run all over an oven on the way to some breakers.
Am I overreacting?
Thanks,
Mike
I used to be an EE, many years ago, so I just got pulled into a review of an old (>70 year) oven on our production floor. I have not looked at the NEC since about 2005 so I am more than rusty. I would appreciate it if I could get a quick reality check.
The oven is supplied with 3 phase 240 by a 150 amp breaker about 25 feet away and power is landed on an abandoned 3 phase contactor with what looks to be 50 year old 2/0. From here, there are many (>10) small gauge (18-12 AWG) wires all smashed together to land on another terminal on each of the poles of the contactor terminals on the same side of the contactor as the landing. (The switched side is abandoned.) These wires then run through the oven, under the heated zone, to another panel with breakers. The entire length of these wires is enclosed in the oven, but not protected in any other way. All of the cloth insulation is fraying. The interpretation seems to be that these wires are taps.
We have an oven in house, but it may take a week or more to get ready to replace the older oven.
I have visions of 36 kW finding a way home through 18 AWG conductors so my instinct was to simply shut down the older oven until the new oven is ready to power up.
Barring this, my basic suggestions were that:
1) While we probably comply with the disconnect requirements, it would take someone that was not familiar with the oven several minutes to find it and we should just put one on the oven at the point of power entry. Short term, we should at least train everyone that works on the floor on the location of the disconnect.
2) If we wanted to run the existing oven, the wires from the 2/0 needed to directly land on some kind of distribution board and directly feed breakers, not run all over an oven on the way to some breakers.
Am I overreacting?
Thanks,
Mike