I just started renovations on an existing building. The main service switch is a 400A, 3P disconnect switch fused at 400A. Off the load side of the switch there are two sets of 2/0 THHN copper per phase. One set of 2/0 runs about 15 feet thru a wireway and terminates in a 200A main circuit breaker protecting a lighting panel. The second set of 2/0 run about 10 feet into the wireway where they are each tapped with (2) #4 THHN copper conductors. Then the two sets of #4 terminate in a 100A,3P disconnect switch which is fused at 100A. This second set, with the 2/0 being tapped by the #4 just doesn't seem right to me. I have read art. 240.21(B) and I can't quite determine if or what it specifically violates. Any help would be appreciated!