Feeder tap

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
In door application... If we want to make a feeder tap, the feeder length is longer than 25 feet from the point of tapping, which rule from NEC should we use? This is not high bay manufacturing building.
 
Unless you fall under the very restrictive 240.90, you are limited to a 25ft tap.
 
In door application... If we want to make a feeder tap, the feeder length is longer than 25 feet from the point of tapping, which rule from NEC should we use? This is not high bay manufacturing building.

You'll need an OCPD within 25' if you're complying with the 25' rule.
 