feeder tapping

Status
Not open for further replies.

frank123

New member
Location
New Jersey
If I come out of a main breaker load side and I go 75', can I install a wire way and tap that feeder. Do I need over current protection before I tap the feeders?
 

david

Senior Member
Location
Pennsylvania
Re: feeder tapping

We would need more information i.e. What size feerder & tap, what is the tap used for , how long will the tap be ,
 

charlie

Senior Member
Location
Indianapolis
Re: feeder tapping

OK I'm going to try this new format. If you are using the correct terminology, you may go 75 feet and then tap the "feeder". This of course is indicating you are following the 240.21 feeder tap rules and it is indeed a feeder. :D
 