Lets say I wanted to tap a 1600A bus with a 500A fused disconnect within 25'.
If I wanted to use 4 runs of 1/0 (3 CCCs in each). Would the EGC need to be 4/0 per conduit or 1/0 per conduit?
Basically, does the rule where the EGC does not need to be larger than the feeder tap conductor reduce the EGC size when taking into account parallel runs or should I consider the feeder tap as the circular mils of 4x1/0 and that brings me back to 4/0 being the smallest size EGC?
What if I chose to have all of the CCCs in one conduit, like 4 x 2/0 (derated at 70% is still okay at 546A). Would my EGC be a single 2/0 or 4/0?