Something I noticed in article 440, is that there is no section for feeder size or feeder short circuit and ground fault protection the same way it is shown in article 430 for motors. Does this mean it's not allowed to feed two AC units from one OCPD and tapping off to provide individual branch circuit protection?
For instance, if I have an AC #1 at 121 FLA / 175A max fuse and AC #2 at 57 FLA / 80A max fuse. Would you be allowed to feed them from one fused switch, then tap off to 175A fuses and 80A fuses for branch circuit protection? What feeder fuse size would you give?
If you were following article 430 for the feeder fuse, it would be 175A (largest unit fuse) + 57A (running amps of remaining units) = 232A, then round down to 225A.
For instance, if I have an AC #1 at 121 FLA / 175A max fuse and AC #2 at 57 FLA / 80A max fuse. Would you be allowed to feed them from one fused switch, then tap off to 175A fuses and 80A fuses for branch circuit protection? What feeder fuse size would you give?
If you were following article 430 for the feeder fuse, it would be 175A (largest unit fuse) + 57A (running amps of remaining units) = 232A, then round down to 225A.