ARTICLE 430.28(1)
SCENERIO
MY TAP IS IN A NEMA 4 ENCLOSURE, LESS THAN 10FT, AND IS NOT FOR A FIELD INSTALLATION.
I HAVE A 1000 AMP BREAKER SERVICING THIS PANEL.
IF I RUN A TAP AFTER THIS BREAKER AM I REQUIRED BY CODE TO PROTECT IT WITH AN OVER CURRENT DEVICE ON THE LINE SIDE OF THE TAP CONDUCTOR, MAKING SURE THAT THE RATING OR SETTING NEVER EXCEED A 1000 PERCENT OF THE TAP CONDUCTOR AMPACITY???
jerryb
Re: FEEDER TAPS
You quoted the NEC almost exactly, except you said "not for field installation" and the NEC says "for a field installation". Can you clarify your question and/or installation?