S shaw0486 Senior Member Location baltimore Jan 14, 2011 #1 Is it permitted by the NEC to tap a 125 amp feeder with 3 # 10 and run it 60' before hitting OCP? What code articles is this?
Is it permitted by the NEC to tap a 125 amp feeder with 3 # 10 and run it 60' before hitting OCP? What code articles is this?
david luchini Moderator Staff member Location Connecticut Occupation Engineer Jan 14, 2011 #2 No, (unless its is an outside tap per 240.21(B)(5).) Feeder tap conductors are limited to 10' in length by 240.21(B)(1) or 25' in length by 240.21(B)(2), (B)(3) and (B)(4). The #10 tap would be limited to 10'. Last edited: Jan 14, 2011
No, (unless its is an outside tap per 240.21(B)(5).) Feeder tap conductors are limited to 10' in length by 240.21(B)(1) or 25' in length by 240.21(B)(2), (B)(3) and (B)(4). The #10 tap would be limited to 10'.