Regarding a feeder to an MCC on a set of plans. The feeder is 350 kcmil, the overcurrent is 400 amps. According to 430, the feeder may be sized at 125% of the FLC of the largest motor and the sum of the FLC of the remaining motors. The overcurrent device protecting the feeder is sized at the largest protective device feeding a branch circuit for a motor, and the sum of the FLC of the other motors. So depending on these calculations, this could be a legal install even though 350 is rated at 310 amps on table 310.16?