Feeder to meter base

Status
Not open for further replies.

RESI

Member
Location
Virginia
Hello to all- I came across a strange situation at a residence. I was looking at this house in Va with regards to changing out the old fused main panel. In VA, code says that the meter base must be within 6 feet of the main panel. I went outside to look at the meter base, and found it located approximately fifteen feet from the main panel (straight line). My question is: Is there a restriction that says the feeder to the meter base from the power company can only be so long? My plans are to install a new meter base within 6 feet and let power company get their feed to it. Thanks to any and all repliers!
 
Yes Sir, that is what I meant to say.

Well see 230.70(A)(1)....With that said and Va. said you can enter into the building 6' then over that one would need to install a disconnect / ocpd on the exterior, then see 250.24(A)(5) would need SER from there. So what confused me was mentioning the POCO? They have nothing to do with the Service Entrance Conductors.
 