I have a 800 amp single phase service (120/240) on a residence.The gear is made by AMP manufacturing and is a CT/Main combo unit SCT8 - 3T. The unit has 3-200 amp breakers and 1-125 amp breaker for distribution.
I think that I can use 4/0 SER Al to feed the 200 amp sub panels based on Table 310.15(B)(6). My inspector says that I need to refer to 334.80, which puts me in the 60 degree column for Alum and that puts me at 300 MCM Al. It seems to me that Table 310.15(B)(6) overrides Table 310.16 on single phase 120/240 volt feeders in residence(dwelling unit). I have read the handbook and Mike Holts changes to 2008 NEC and still think that I am correct. However my inspector is AHJ and says otherwise.
Does anyone have any input ?
I think that I can use 4/0 SER Al to feed the 200 amp sub panels based on Table 310.15(B)(6). My inspector says that I need to refer to 334.80, which puts me in the 60 degree column for Alum and that puts me at 300 MCM Al. It seems to me that Table 310.15(B)(6) overrides Table 310.16 on single phase 120/240 volt feeders in residence(dwelling unit). I have read the handbook and Mike Holts changes to 2008 NEC and still think that I am correct. However my inspector is AHJ and says otherwise.
Does anyone have any input ?