I am working on the design of an outpatient clinic, essentially a medical office building type of facility, located in a building that used to be a hospital, recently reclassified as Business Use. Against my advice, the client wants to save money by utilizing existing feeders to this space all of which consist of 3 phase and a neutral, utilziing the rigid steel conduit as the ground. Here are my questions:
1. The requirements of a redundant ground for healthcare facilities notwithstanding, is it still permissible to use the conduit as a ground?
2. Since it is a healthcare facility, patient care area's need to be wired in accordance with 517.13, i.e. with a redundant ground. Does that redundant ground have to go all the way back to the source. I would think that the answer is yes and therefore the existing feeder, lacking as it is of an insulated equipment grounding conductor would render this installation non-compliant. Do you agree?
Thanks,
Mike
1. The requirements of a redundant ground for healthcare facilities notwithstanding, is it still permissible to use the conduit as a ground?
2. Since it is a healthcare facility, patient care area's need to be wired in accordance with 517.13, i.e. with a redundant ground. Does that redundant ground have to go all the way back to the source. I would think that the answer is yes and therefore the existing feeder, lacking as it is of an insulated equipment grounding conductor would render this installation non-compliant. Do you agree?