ktm400sx said:I have a 400 amp breaker that I'm using to feed a MCC. Can I apply 240.4 (B) and use 1x 500mcm per phase?
This will give me 380 amps according to 310.16 at 75 deg c
The breaker is rated 40 deg C .....how does this effect the wire size?
Thanks for any help
If the caculated load is 380 amps or less then you can use the 500 kcm.ktm400sx said:I have a 400 amp breaker that I'm using to feed a MCC. Can I apply 240.4 (B) and use 1x 500mcm per phase?
This will give me 380 amps according to 310.16 at 75 deg c The breaker is rated 40 deg C .....how does this effect the wire size?
Thanks for any help
ktm400sx said:..Can I ..use 1x 500mcm per phase? This will give me 380 amps according to 310.16 at 75 deg c
infinity said:The 40 degree C rating is for the ambient temperature of the breaker not the terminals.
I think not. A breaker is rated for its rated rating.mike0w said:. . . but if the breaker is a standard molded case breaker are rated for 80% of the breaker rating in this case 320A so 500's would be fine. . . .
ramsy said:Motors require other considerations not mentioned yet.
ramsy said:
2. If those motors run continuous, load x 1.25, that #500 may be too small.
charlie b said:
A breaker is rated for its rated rating.