I have a cabinet that controls two motors. M1: 100hp 460V 3phase. M2: 40hp 460V 3 phase. M1 uses 2/0 and controlled by VFD, fuse protected at 200 amps (Altivar recommended). M2 uses 6 AWG overload protection and motor starter, fused at 90 amps. The feeder comes from a 400A instantaneous breaker, 4/0 conductors into the cabinet disconnect rated at 400A (non fusible). Then goes through a distribution block and branches off to the 2 motors. Question: Is it ok to use 4/0 (wire sized for the load) with a feeder breaker 400A instantaneous? That breaker was all that was available and we even called GE to verify our application. Thanks for any help.