Feeder with no L-N loads & 215.2(A)(2)
tortuga
Code Historian
Oregon
Electrical Design
Greetings group
I am looking at upsizing a existing feeder, for adding a new load,
and I have an EMT existing pipe run.
The panel only feeds 240V loads, plus the load I am adding is only 240V.
(There is lighting panel right next to this panel that has a neutral.)
I don't usually like to stuff conduits to their max but this might save the customer some money.
If I have only 3 conductors in the pipe I could in theory get away with it and be under max fill.
The pipe is currently the EGC, and there is a neutral bus in the panel with nothing connected.
That 3rd wire would be better used as an redundant EGC.
I am probably going to solve this another way by relocating some equipment, but
It all got me wondering is a grounded conductor even required in a feeder?
I am thinking yes per 215.2(A)(2),
Thoughts opinions?
Absolutely compliant. I educated an inspector about this when I added a feeder and panel to a house for a tankless water heater. I used only SE cable, using the bare conductor as the EGC, and removed the neutral bar.
Curious as to why you removed the neutral bar?
JAP>
To make it more obvious that there is no neutral, and only the EGC bar is available.
I used eight of twelve spaces in a 200a ML panel. Someone might try to add loads.
You're making it too easy on those who don't know any better Larry,,,,, :)
Jap>
Jap>
Yeah, well I have seen it where people have added to that equipment bar for 120v circuits. So Larry did a smart thing. I would also label the panel as 240V only
That's just another cautionary measure taken to make it easier on those who don't know any better. :)
JAP>