Greetings group
I am looking at upsizing a existing feeder, for adding a new load,
and I have an EMT existing pipe run.
The panel only feeds 240V loads, plus the load I am adding is only 240V.
(There is lighting panel right next to this panel that has a neutral.)
I don't usually like to stuff conduits to their max but this might save the customer some money.
If I have only 3 conductors in the pipe I could in theory get away with it and be under max fill.
The pipe is currently the EGC, and there is a neutral bus in the panel with nothing connected.
That 3rd wire would be better used as an redundant EGC.
I am probably going to solve this another way by relocating some equipment, but
It all got me wondering is a grounded conductor even required in a feeder?
I am thinking yes per 215.2(A)(2),
Thoughts opinions?