I am looking at upsizing a existing feeder, for adding a new load,
and I have an EMT existing pipe run.
The panel only feeds 240V loads, plus the load I am adding is only 240V.
(There is lighting panel right next to this panel that has a neutral.)
I don't usually like to stuff conduits to their max but this might save the customer some money.
If I have only 3 conductors in the pipe I could in theory get away with it and be under max fill.
The pipe is currently the EGC, and there is a neutral bus in the panel with nothing connected.
That 3rd wire would be better used as an redundant EGC.
I am probably going to solve this another way by relocating some equipment, but
It all got me wondering is a grounded conductor even required in a feeder?

I am thinking yes per 215.2(A)(2),
Thoughts opinions?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The panel only feeds 240V loads, plus the load I am adding is only 240V.

If I have only 3 conductors in the pipe I could in theory get away with it and be under max fill.
The pipe is currently the EGC, and there is a neutral bus in the panel with nothing connected.

It all got me wondering is a grounded conductor even required in a feeder?
Absolutely compliant. I educated an inspector about this when I added a feeder and panel to a house for a tankless water heater. I used only SE cable, using the bare conductor as the EGC, and removed the neutral bar.
 

jap

Senior Member
Occupation
Electrician
Absolutely compliant. I educated an inspector about this when I added a feeder and panel to a house for a tankless water heater. I used only SE cable, using the bare conductor as the EGC, and removed the neutral bar.


Curious as to why you removed the neutral bar?

JAP>
 

jap

Senior Member
Occupation
Electrician
To make it more obvious that there is no neutral, and only the EGC bar is available.

I used eight of twelve spaces in a 200a ML panel. Someone might try to add loads.


You're making it too easy on those who don't know any better Larry,,,,, :)

Jap>
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You're making it too easy on those who don't know any better Larry,,,,, :)

Jap>

Yeah, well I have seen it where people have added to that equipment bar for 120v circuits. So Larry did a smart thing. I would also label the panel as 240V only
 

jap

Senior Member
Occupation
Electrician
Yeah, well I have seen it where people have added to that equipment bar for 120v circuits. So Larry did a smart thing. I would also label the panel as 240V only

That's just another cautionary measure taken to make it easier on those who don't know any better. :)

JAP>
 