I have an old switchgear I am installing a 400 Amp fused disconnect in. 150 feet from that switchgear I am installing a 400 Amp panelboard. The incoming service is a 120/240 Delta 3 Phase system. All I need is 3 phase for 2 10 ton roof top AC Units. We have determined we can do this with 150 amps of service. I had the panelboard manufactured so these two breakers for the AC Units is all that can be installed on the high leg. The rest of the panelboard is for general purpose 120/240 single phase loads. What I have done is pull 2 500 kcmil for the single phase and 2 of the phases of the AC to the panel board. I pulled a 4/0 for the high leg and a 4/0 for the neutral( being the maximum unbalanced load will be 200 amps). I am fusing the 500's at 350 Amps and the 4/0 at 200. I also pulled a number 3 thhn conductor for a ground. Is there anything in the code which says I cant do this? I have checked with the city inspectors here and they looked for three days and couldnt find anything and my bosses cant come up with anything. Message me back please with an answer. Thankyou very much, Leamon