feeders ampacity

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
A drawing would help
What size is the house service?
Is there a sub panel off the service that feeds the garage?
How much load are you adding and is the dwelling all electric, or gas, etc
 
Location
lynnwood washington
Occupation
electrician
200 amp at house panel , garage sub is fed with #4 copper currently fused at 60 a from the house . my question is can i upsize breaker at house panel to 100 a in accordance with allowable ampacities based on 310.12a for services and feeders or am i stuck with 310.16. the load currently at garage is almost nothing , a door opener , 2 plugs and a light. and yes its for a EV charger .
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
200 amp at house panel , garage sub is fed with #4 copper currently fused at 60 a from the house . my question is can i upsize breaker at house panel to 100 a in accordance with allowable ampacities based on 310.12a for services and feeders or am i stuck with 310.16. the load currently at garage is almost nothing , a door opener , 2 plugs and a light. and yes its for a EV charger .
No.

What is the current draw for the charger?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
200 amp at house panel , garage sub is fed with #4 copper currently fused at 60 a from the house . my question is can i upsize breaker at house panel to 100 a in accordance with allowable ampacities based on 310.12a for services and feeders or am i stuck with 310.16. the load currently at garage is almost nothing , a door opener , 2 plugs and a light. and yes its for a EV charger .

#4 THHN is rated at 85 amps @75° C. Next size up would be 90 amp OCPD.
 

paullmullen

Senior Member
Location
Wisconsin
Occupation
Electrical Engineer & Master Electrician
Just an attempt at a full checklist:
1) Do you have the right Overcurrent Protection Device in the house panel? (Thanks @infinity )
2) Do you have have the correct main disconnect OCPD in the garage?
3) Does the feeder ampacity need to be corrected for the conduit? (probably not with three or less current carrying conductors).
4) Verify that ground and neutral are separated except in the main panel.
5) Verify grounding system at the garage is in place (rods, plate, ufer, whatever).
6) Are there any local modifications to the NEC required by AHJ?

What else am I missing?
 