feeders and nipples

Status
Not open for further replies.

garrisonm1

Member
Location
Maryland
I have two tubs (panels) side by side with one nipple in between the two. Through that nipple I have the feeders (jumpers) feeding the other panel. My question is am I allowed to run any branch circuits through that same nipple if the spacing allows it. If not what artcle # is that and what % of that nipple can be filled. thanks

greg
 

charlie

Senior Member
Location
Indianapolis
Re: feeders and nipples

Go for it, nothing prohibits a branch circuit and feeder conductors in the same raceway. There is a prohibition from installing service conductors and feeders or branch circuits in the same raceway though.
 