Don Miller
New member
- Location
- Fresno, CA,
I work for multple colleges, we recently had a contractor install a replacement panel in one of our machine shops. This panel is a 400A. 208/120Y. Prior to 2nd walkthrough inspection ( the panels were all open) I noted to the contractor that it would be very difficult to perform service on any of the branch circuit conductors or replace any branch, circuit breaker in the future due to installing the #4/0 parallel feeders after the branch circuits were terminated. The #4/0's are coming from the top of the panel to a bottom mounted main-breaker. These conductors are effectively covering access. Also, the EGC's which are multiple#2's/4's are tied down in front of the branch circuit conductors on the opposite side of the panel. I have never installed in this manner, it does not make sense, yet ,the AHJ,myself and the engineer have found no code violations. All I can cite at this point is workmanship/standards and that is still not an acceptable reason for the contractor to correct what I believe is a no-brainer. I am very frustrated as I am thinking back on my days in construction, knowing that if I had installed in this manner, it would not have passed.