we installing new meter pan for a cable company at Manhattan, some times we tap at the end line box, copper detail, and if we have already six main disconnects we tap of the load side of any existing main disconnect as as secondary disconnect using the tap rules, 10ft from the tap and 10% minimum of the wire, example: from the OCPD is 800A on the main disconnect the 10% is 80A so we using #4 THHN for the tap conductors and because is NYC we use #6 THHN for the EGC. the inspector fail my site because the EGC is no rated for 800A on the 250.122 table that is a 1/0 but if i go by the tap rules my site of the tap feeders is correct but if i install 1/0 EGC we will fail inspection because the EGC can no be bigger than my feeders and in 250.122(g). so my question is what size EGC do I have to use because is a very confusing language in the NEC.