I have a transformer which is supplying power to a 480V MCC bus. The MCC bus is rated for 2000A and the LV breaker coming off of the transformer feeding the cables over to the MCC is a 2000A breaker. My question is, can the feeder cables be rated to the exact bus size of 2000A or do the feeders have to be rated at 2000A plus 125%. The MCC bus has both continuious and non-continuous loads. I was looking at section 215.2(A)(1) of the NEC and it seems like you would need to have the feeders rated at 125% of the bus. There is also an exception below this which refers to an overcurrent device but I'm not sure if it applies in my case. What would the cables have to be rated for in my case? 2000A exactly or more?