deerhead said:I have customer (Maintenance Electrician) that is insisting to feed a 1200A distribution panel with (2) 600A breakers. Where do I start to look in the NEC for the article that tells me that this not practical? Or is this practice actually possible?
No where in the NEC that I know of. It deals very little with "practical" or "possible".deerhead said:... Where do I start to look in the NEC for the article that tells me that this not practical? Or is this practice actually possible?
That's not much information to give you a batch of absolutes. I would have to make too many assumptions to arrive at their conclusions.(cut) feed a 1200A distribution panel with (2) 600A breakers.
don_resqcapt19 said:I don't think it is valid with the information that has been provided. It appears to me that they are atempting to serve a 1200 amp load with two 600 amp breakers connected in parallel.
The difference is that a double ended LV switchgear line-up is designed to be capable of operating in this capacity, and it would have proper system coordination such that breaker interlocks would trip and block close during a fault on one side or the other to isolate. The bus and mains would also be rated to carry the full capacity. You could also probably guarantee that only qualified personnel would be working on it.Cold Fusion said:So, q, charlie, king, explain why this is different from a double ended sub with a full capacity tie, run with the tie closed. Are there design concerns? Sure. Do they have to be addressed? Yes.
cf
brian john said:1. Why?
2. Is this redundant feeds from different sources and one CB is always open.?
kingpb said:(cut) What is being described in the OP does not sound like it fits into this category. (cut)[/(quote]
Excellent description. The part about the OP's system may even be true. Probably is. That doesn't change that you guys are reading a lot (a few hundred words in fact) into the nine word phrase the OP used to describe the request.
For example, I can't tell how you (plural and collectively) know the load on the 1200A panel is greater than 600A
cf
edited to clarify
deerhead said:I have customer (Maintenance Electrician) that is insisting to feed a 1200A distribution panel with (2) 600A breakers. Where do I start to look in the NEC for the article that tells me that this not practical? Or is this practice actually possible?