I am spec'ing a job right now to replace a 220v window unit that currently services the third floor of a ca. 1900 house with a pair of Mitsubishi mini splits. There is currently a single, 12-2 (romex) 20A circuit servicing the window unit that I'd like to reuse, as getting power to the area needed will be a PITA, but I'm not sure I could make it work for BOTH units. If reused, I'd have it feeding a separate FUSED disconnect for each unit fused at 15A. The nameplate data for EACH unit is:
MCA 12A
MOCP 15A
RLA 6.6A
LRA 8.2A
Outdoor fan 0.5A
Indoor fan (powered off the outdoor unit) 0.76A
If it weren't for the MCA being listed, the existing circuit would be sufficient. However, as I read 440.6(A), it looks as though the MCA must be used for sizing, though I'm not sure if it is the number used for sizing loads when multiple pieces of equipment are used. I'm thinking that since the MCA accounts for the 125% of the first motor load, I should be able to add the 12A MCA from the first motor to the 6.6, 0.5, and 0.76 of the second unit (total of 19.86). If I must use the sum of the MCA from both units, then I'm at 24A, which is over capacity for #12 NM-B. What am I missing?
MCA 12A
MOCP 15A
RLA 6.6A
LRA 8.2A
Outdoor fan 0.5A
Indoor fan (powered off the outdoor unit) 0.76A
If it weren't for the MCA being listed, the existing circuit would be sufficient. However, as I read 440.6(A), it looks as though the MCA must be used for sizing, though I'm not sure if it is the number used for sizing loads when multiple pieces of equipment are used. I'm thinking that since the MCA accounts for the 125% of the first motor load, I should be able to add the 12A MCA from the first motor to the 6.6, 0.5, and 0.76 of the second unit (total of 19.86). If I must use the sum of the MCA from both units, then I'm at 24A, which is over capacity for #12 NM-B. What am I missing?