Can I feed three 100 amp, single phase 3-wire 120/208V apartments using a 3 phase 4-wire 208V 100 amp circuit?
Here's my worse case scenario calculation:
100Ax208V x 3 apartments = 62,400VA
Per NEC 220.84 to find 3 phase feeder:
62,400VAx0.45 = 28,080VA
28,080VA/(208V√3) = 78 amps
Calculated 3-phase feeder is 78 amps but I will make the minimum to 100 amps since each apartment is 100amps.