It's not at all uncommon for marinas to need fire pumps, because the Coast Guard will not fight dock / marina fires or fires on boats that are docked, so the local fire depts. have jurisdiction.
But being that you are posting it here, I take it they want an electric fire pump? That part is a bit unusual, because typically on a marina facility you want the fire pump to be mobile and engine powered because if the fire takes place between the shore and the pump (or in this case hydrant), you might get cut off from access to it. Also if the pump is on the dock, there may be a conflict with GFCI issues and you don't want a GFCI tripping a fire pump off line, nor do you want an electrical problem in the water in case people jump in to escape fires. That's why as Electricians, we rarely see calls for them.
Are the hydrants on land then? If so, I take it the pump will be on land then too, so basically it's just like any other Fire Pump controller, only NEMA 4X if exposed outdoors. Might be cheaper (and safer) for them to consider building a little block house for it and the pump and using a standard indoor unit.
In most cases, the Fire Pump supplier will be tasked with supplying the starter for it, because there are a lot of decisions about selecting the pump that also play into selecting the right starter and starting method. Most likely all you need to deal with is the source connections per the NEC requirements in Article 695 / NFPA 20 and any ATS issues, assuming there is a back-up generator.
thanks for the reply. i went over and looked at it. there's about four colors of fugly
smeared all over it:
there's a stamped set of drawings on it, but no specifications on electrical install of pump.
there are two hose cabinets with a 2 1/2" gal pipe connecting them..... to domestic water.
2 1/2" wasn't specified on drawings. domestic water to the facility is 2" at the property
line. only 1 1/2" out to the dock. doesn't appear to match engineered drawings,
which don't seem to reflect the occupancy, either.
power to the facility is 1950's, 200 amp single phase 240 volts, a gutter fed off a
fused disconnect. no means of tapping ahead of the main except punching into
POCO meter cabinet. pump referenced on drawings is 3 phase.
you could put the fire pump on land instead of the dock, but then you'd have to pipe
the fire line another 300' or so.... which you'd have to do anyway, if you don't want
to feed the fire main off the dock domestic water, which seems to be 1 1/2".
the pump specified, from the mfg. cut sheet shows these following uses.
no specific fire pump controller is mentioned:
Residential, Commercial Cast Iron, Bronze Fitted
Centrifugal Pumps G&L Series 3656/3756 S Group
Applications:
Booster service
Spraying systems
Irrigation
Water circulation
Liquid transfer
General purpose pumping