feeding a sub panel

Status
Not open for further replies.

Rinpo

Member
Location
America
Occupation
Sparky
Does electrical code allow running parallel sets of feeder wires in seperate conduits? I have 3 2" conduits below a desired location for a subpanel in a residential dwelling, but they are too small for 4/0 conductors. I'm wondering if I can run either 2 of each conductor in separate conduits or run a set of each in 2 conduits. If so, can I splice them from 4/0 conductors to 2 sets of small diameter conductors in an exterior pull box, or do they need to come from the service in 2 sets.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Even with Sched. 80 PVC, one 2" conduit is large enough for three 4/0s and a #4.

If you choose to parallel, you should have a full set (L, L, N, G) in each conduit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Does electrical code allow running parallel sets of feeder wires in seperate conduits? I have 3 2" conduits below a desired location for a subpanel in a residential dwelling, but they are too small for 4/0 conductors. I'm wondering if I can run either 2 of each conductor in separate conduits or run a set of each in 2 conduits. If so, can I splice them from 4/0 conductors to 2 sets of small diameter conductors in an exterior pull box, or do they need to come from the service in 2 sets.
How many amps is the feeder?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Does electrical code allow running parallel sets of feeder wires in seperate conduits? I have 3 2" conduits below a desired location for a subpanel in a residential dwelling, but they are too small for 4/0 conductors. I'm wondering if I can run either 2 of each conductor in separate conduits or run a set of each in 2 conduits. If so, can I splice them from 4/0 conductors to 2 sets of small diameter conductors in an exterior pull box, or do they need to come from the service in 2 setsts

No , all conductors of the circuits must be together so one conduit would need 2 hots and a neutral & possible equipment grounding conductor while the other would be the same but

What kind of sub panel is this for a residence. Also I believe 2- 4/0 and a smaller neutral and an equipment grounding conductor would probably fit in one 2" conduit.

Look at 300.4(B) and then 310.10(H)
 