Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
If a panel has a particular size MCB and the total connected load is obviously lower do you still need to have wiring rated for MCB size regardless of connected load?
If a panel has a particular size MCB and the total connected load is obviously lower do you still need to have wiring rated for MCB size regardless of connected load?
The protective device at the begining/source of the conductors, or the rules in 240.21(B).If you don't size the wiring to the capability of the MCB's OCPD, what's going to protect the wiring?
JAP>
Is this panel the service equipment? If not, how does it get its power?If a panel has a particular size MCB and the total connected load is obviously lower do you still need to have wiring rated for MCB size regardless of connected load?
Conductors need to be protected at their source except when following the rules in 240.21(B).I don't think he's talking about an upstream overcurrent protection device.
I think he's asking if you have a panel that's drawing 30 amps but has a larger Main can you size the wiring to the main at 30 amps.
I say no.
JAP>
Is this panel the service equipment? If not, how does it get its power?
I don't think that this is a service, so if the panel is 225 amps with a 225 amp main but the calculated load is 100 amps then a 100 amp feeder can supply the panel.
It not being a service is an educated guess.I still don't understand where you all are coming up with a "Feeder" based on the OP"s opening statement.
What if this is a service panel directly behind a meter where the Main is the one and only OCPD?
How could you size the wire feeding the 225amp main breaker from the meter at only 100 amps ?
JAP>
Because the OP used the words "Feeding" in his title. That, to me, indicates a feeder.I still don't understand where you all are coming up with a "Feeder" based on the OP"s opening statement.
What if this is a service panel directly behind a meter where the Main is the one and only OCPD?
How could you size the wire feeding the 225amp main breaker from the meter at only 100 amps ?
JAP>
Yes, feed a 225 amp panel with a 60 amp ocpd and #6 conductors if the calculated load is 60 amps.Source OCPD feeding MCB panel. I referring to the MCB in the panel in this scenario . So your saying wire needs to be sized to the OCPD at this source in this scenario? This is not a service .
So to be clear, except for service , when feeding from source OCPD to another panel OCPD the feeder/wire size needs to be sized to the source OCPD and the calculated load your feeding obviously can’t be higher than the source OCPD?Yes, feed a 225 amp panel with a 60 amp ocpd and #6 conductors if the calculated load is 60 amps.
Short answer yes.So to be clear, except for service , when feeding from source OCPD to another panel OCPD the feeder/wire size needs to be sized to the source OCPD and the calculated load your feeding obviously can’t be higher than the source OCPD?
So to be clear, except for service , when feeding from source OCPD to another panel OCPD the feeder/wire size needs to be sized to the source OCPD and the calculated load your feeding obviously can’t be higher than the source OCPD?
Because the OP used the words "Feeding" in his title. That, to me, indicates a feeder.
Thanks professor!"Feeding" is simply a much simpler way to say "I'm going to extend wiring from one source to another..
"Feeding" should never be confused with our definition of "Feeders", Taps, Branch Circuits and Service Conductors.
JAP>