I have this installation where we cannot shutdown the maingear or do any changes to existing wirings.
the client wants to install two 75kva delta-Y 480v-208v transformers. the existing gear has (1) 225A (#2/0 conductors) CB and (1) 200A CB (#250MCM conductors) that are spares/unused.
1. can I use one of the two CBs to feed the two 75kva transformers?
2. if I must use both CBs for this installation, how can i work around not being able to change the CBs/Wire sizes. i.e, if we decide to use the 225A (#2/0 conductors) CB, can I run those to a 175A fused disconnect then continue with the installation as normal?
and, if i use the 200A CB (250MCM) shall I run the wires into a 125A fused disconnect and then reduce the wire size based on the disconnect rating then continue with the installation normally?
thanks!!