Fence grounding
donblasy
I am looking for guideance grounding two and one half miles of plastic coated chain link fence. It has three strands of barb on the top, the barbs are exposed metal but the cable is plastic coated also. If a ground is attached to a post, only that post will be grounded because of the plastic coated ties and insulation. Any helpfull suggestions would be appreciated.
don_resqcapt19
Illinois
retired electrician
Where is this fence installed at? If it is under or very close to high voltage transmission lines it may require grounding.
Don
don_resqcapt19
Illinois
retired electrician
The fence is installed at a chemical plant and is part of Homeland Security requirements
In that case you many want to isolate and energize it:D
There is no code rule that would require this fence to be grounded.
Don
George Stolz
Windsor, CO NEC: 2017
Service Manager
Don
Can you elaborate? I have a fence pretty close to HV transmission lines.
don_resqcapt19
Illinois
retired electrician
George,
In that case, it is possible that you can have enough voltage induced on the metal fence to be a shock hazard. In most cases, an all metal fence with metal poles would not have this problem, but a metal wire fence on wooden poles may have this type of problem. While not exactly the same there is some information on this problem here. The information starts on page 2 of the PDF. Section 5 of the document (p14) talks about the shock hazard.
Don
brian john
Leesburg, VA
Homeland Security
And there lies the problem, someone thinks this is a safer installation, so it makes specs and next thing you know non-UL-listed ground rods are being driven all over the country, the non listing is discovered all those rods MUST be removed and UL listed rods installed..Money for some contractor.