Few questions on receptacles.

Status
Not open for further replies.

JohnDS

Senior Member
Location
Suffolk, Long Island
Occupation
Electrician
1) Within how many feet do you need a receptacle from a/c condensors?

2) Is it permissable to have garage receptacles wired in 14awg on a 15a circuit as long as they're GFCI protected?

3) Do garage door openers need to be on a dedicated circuit each?
-If so, is it permissable to put 2 or even 3 of them on the same circuit as long as all three do not max out the circuit?

-Do they have to be wired in 12awg 20amp or can you use 14awg 15a?

-Is it legal to tap off a garage lighting circuit or the garage receptacles to power a single garage opener?
 
JohnDS said:
1) Within how many feet do you need a receptacle from a/c condensors?
25 feet : 210.63
JohnDS said:
2) Is it permissable to have garage receptacles wired in 14awg on a 15a circuit as long as they're GFCI protected?
Yes
JohnDS said:
3) Do garage door openers need to be on a dedicated circuit each?
No
JohnDS said:
-If so, is it permissable to put 2 or even 3 of them on the same circuit as long as all three do not max out the circuit?

-Do they have to be wired in 12awg 20amp or can you use 14awg 15a?
Depends on the load(s)
JohnDS said:
-Is it legal to tap off a garage lighting circuit or the garage receptacles to power a single garage opener?
Legal.
 