Fiber Conduit

Status
Not open for further replies.

laketime

Senior Member
I am installing some underground for future fiber optic cables. There are no specs. What is usually the minimum radius on a 2" pvc conduit run for fiber.
 

kameele

Member
Location
NH
the Corning FO I've been speccing recently (FREEDM series) requires a bend radius of 3.8" for pulling and 2.5" for installed. This is a 6 fiber, tight buffered cable. the 24 fiber goes to 6.5"/4.3".
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The minimum permitted bending radius for 1.25" conduit is 7.25". As the conduit size gets larger the minimum bending radius also gets larger. You should have no issues with the bend radius of the conduit.
 
Status
Not open for further replies.
Top