Flyinbryan
Member
- Location
- Houston, TX
Here is a unique situation I have I need help with. I have a fiber cable that is armor with a PE jacket for outdoor use. This cable does not carry a FOC or a FON rating due to it being for outdoor use. It was originally intended to be direct buried. The client decided to put it in a ductbank instead due to direct burial requirement in the specs being too deep. I created a 6" sleeve in concrete and I have put this armor fiber cable in the same conduit with a 600V power cable that is also armor and carrying a 110VAC circuit. Both are for CCTV camera use around the perimeter of a PE plant. They are saying I am in violation of NEC 770.133. However, this only pertains to indoor use rated cable that is always marked FOC or FON. The manufacturer of this fiber optic cable is saying the power circuit (110vac) can induce a voltage through the 600V jacket, through the armor around the power cable jacket , then through the PE jacket around the fiber cable into the armor of the fiber cable and create a safety issue. Do I have an argument here that it won't happen or do I have to pull all this fiber out and run another 6" conduit 3 miles? Thanks in advance.