110819-0802 EDT
How does the speed of an unloaded DC shunt field motor vary relative to the current in the field?
Induced voltage in the armature of a DC motor or generator is proportional to RPM and flux density. In generator mode this means that at fixed speed the output voltage increases as the flux density increases, and flux density is proportional to current up a saturation region.
In motor mode the counter EMF (induced voltage is the armature) closely equals the applied voltage. The difference of these two voltages is the I*R drop in the armature due to load current, a small value.
Thus, in a DC shunt motor if the flux density is reduced the motor runs faster. If current to the field is lost, then under unloaded conditions the motor speed may rise to a level where the centrifugal force tears apart the armature.
The purpose of the field loss relay is to monitor the field current and if current is lost remove power to the motor armature to mechanically protect the motor.
.