In a meter can, what is the fifth jaw for? Can I use a five jaw meter can in a four jaw application? is the fifth jaw removable?
5th jaw is for neutralIn a meter can, what is the fifth jaw for? Can I use a five jaw meter can in a four jaw application? is the fifth jaw removable?
I think it is needed when using on a 208/120 system with only two phases and neutral being metered. Not certain exactly how the metering works but with 120/240 and 180 degree phase angle you can meter accurately by monitoring only the two ungrounded conductors, but the 120 degree phase angle of the wye system has inaccuracies if only using a 4 wire meter so it needs a neutral reference to be accurate. Same should be true on any other wye system though 208/120 is the most encountered where you might see only two phases plus a current carrying neutral.
DittoHere the POCO has always required 5 jaws for everything with the 5th jaw in the 9 o'clock position.
-Hal
I have rarely ever seen a 5 jaw meter socket except on single phase supplied by 208/120.Here the POCO has always required 5 jaws for everything with the 5th jaw in the 9 o'clock position.
-Hal
If it's a new area to you . Usually the counter guys at the local supply house will tell you what you should install.In a meter can, what is the fifth jaw for? Can I use a five jaw meter can in a four jaw application? is the fifth jaw removable?
Good point, they do.If it's a new area to you . Usually the counter guys at the local supply house will tell you what you should install.
They may not know why, But they'll say this is what everybody buys...
I'm installing a meter main at a residence. I consulted the book from the POCO that lists the allowable units. I was having a hard time finding a unit I can use. I found one that is a five jaw and is listed as allowed for residential, but I've never seen a five jaw meter can in use at a residence. I wasn't sure if there was some other criteria I need to know about like it can only be used for 120/208 services. It doesn't list any other criteria in the book. I thought maybe if the fifth jaw was removable and I removed it, I wouldn't get turned down by the POCO when they come to inspect.
It really shouldn't matter. If the meter doesn't have the fifth tab it will still plug in. That don't mean some POCO guys won't insist you need a 4 jaw meter though.I'm installing a meter main at a residence. I consulted the book from the POCO that lists the allowable units. I was having a hard time finding a unit I can use. I found one that is a five jaw and is listed as allowed for residential, but I've never seen a five jaw meter can in use at a residence. I wasn't sure if there was some other criteria I need to know about like it can only be used for 120/208 services. It doesn't list any other criteria in the book. I thought maybe if the fifth jaw was removable and I removed it, I wouldn't get turned down by the POCO when they come to inspect.
Can you post the approved units?I'm installing a meter main at a residence. I consulted the book from the POCO that lists the allowable units. I was having a hard time finding a unit I can use. I found one that is a five jaw and is listed as allowed for residential, but I've never seen a five jaw meter can in use at a residence. I wasn't sure if there was some other criteria I need to know about like it can only be used for 120/208 services. It doesn't list any other criteria in the book. I thought maybe if the fifth jaw was removable and I removed it, I wouldn't get turned down by the POCO when they come to inspect.
Can you post the approved units?
I know you don't like shopping online, but you might need to. Have you checked to see if Home Depot can order it?
You need a 12S or 25S meter for this.My GC is in a hurry. I can order several different units at Home Depot, but it will take a week. I found a useable unit at a local supplier. They have to ship it in from a warehouse overnight. (I don't have an account so I'm paying too much.) It's listed in the POCO guide as a 4/5 jaw. I hoping this means the fifth jaw is removable. The link below from Greybar lists it as a five jaw.
https://www.graybar.com/meter-main/p/97136111
I believe that depends on design of the meter?Yup, a regular residential meter has a known error if there is imbalance between the sides of a 120/240V single phase system, but this error is usually quite small.
If you were to load up only one if the legs with 120V loads only and there were large voltage drop in the service then this could be a significant error.
A 5 jaw meter measures both legs separately and will work for 120/240 but is needed for 120/208.
Jon
I seen CT metering on 120/240 single phase that only uses one CT, and each ungrounded conductor passes through in opposite direction, making the meter effectively only see 120 volts at whatever current it is measuring. any 240 volt loads get doubled by passing the conductors in opposite directions through the CT and still would see accurate power level registered on the meter (2x current but still at 120 volts)