sparkyguy545
Member
I recognize Figure 310.60 references Tables 310.77 through 310.86 which are for > 2kV. My question is in regards to the Note on the lower left of the page regarding maximum burial depth. Can someone clarify what I do if I need to exceed "Maximum depth to the top of electrical ductbank shall be 750 mm (30 in) . . ."? This seems like a shallow amount of cover for a Medium Voltage ductbank. What if field conditions require 42" or 48" cover? Is it stating that the Ampacities only apply at the published conditions, or that I cannot increase the amount of cover beyond 30"?