I am running parallel 500 MCM copper run 624 feet in lenght ...Need to figure out the voltage drop with a 120/208 volt 3 phase system ..Please give the formula or where I can find it....thank you
Re: figure out voltage drop for a parallel run.
You will need to know the expected load that will be on these conductors before a voltage drop can be figured.
it will be a 600amps main circuit breaker....
Vd = 1.732 x I x D x Rf
Rf = Resistance per foot (From chapter 9, table 8, ohms/kFT devided by 1000)
D = distance
I = Current
Vd = Voltage drop
Divide Vd by 2 for equal size parallel conductors.
I get 8.6 volts or 4.1%.
Cool toy. I book marked it.
Edit: No mention of parallel though.
And it's not as accurate as what I posted. (At least based on table 8)