Fill Rite Pumps

Status
Not open for further replies.

dlhoule

Senior Member
Location
Michigan
Please help me save a lot of time. Does anyone know off hand what the minimum distance from the unit for seal off fitting? I will be wiring a new unit on above ground tank for gasoline. Model FR702R.
 
514.9 Calls for a sealing fitting in each conduit run entering a dispensor and is to be the first fitting after the conduit emerges from the earth or concrete. Don't forget your switched neutral CB
 
tom baker said:
514.9 Calls for a sealing fitting in each conduit run entering a dispensor and is to be the first fitting after the conduit emerges from the earth or concrete. Don't forget your switched neutral CB

Thanks, Tom.

This conduit is all above ground and the wall it comes through is Steel Siding. There is to be a 2 pole disconnect just inside the wall. It is coming from a single pole breaker inside of building to disconnect inisde of building and running from there along a fence which is below a cooling tower. Tank is above ground about 10 feet from fence.
 