Fill Table Anomaly
dkidd
here
PE
We ran across this yesterday.
From Chapter 9 Table 1, allowable fill for 2 wires is 31%.
From Chapter 9 Table 4, allowable fill for 1-1/2" is 0.631 square inches.
Given 2 4/0 THHN
From Chapter 9 Table 5, area of one conductor is 0.3237
Two conductors would be 0.6474
Therefore, two 4/0 would require a 2" EMT.
Annex C Table C.1 says that two 4/0 can fit in 1-1/2".
The amount of fill would be 31.8%.
Throw in a 6AWG THHN ground, the allowable fill is 40%, and a 1-1/2" works, with 34.3% fill.
infinity
New Jersey
Journeyman Electrician
Given 2 4/0 THHN
It's just the way the math works with 31% and 40% fill.
I think that Dennis meant 40% for Annex C.
wwhitney
Berkeley, CA
Retired
Given 2 4/0 THHN
Seems like Chapter 9, Table 1, Note 7 would apply: 0.631 / 0.3237 = 1.949, round up to 2.
Cheers, Wayne
dkidd
here
PE
Thanks, that was the missing factor in my spreadsheet. I've got that incorporated now.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
You would think I remembered this since I made the new tables with corrections etc. I check my spreadsheet and yes it covers all situations. I spent a long time on that info and my brain forgot it all.... I'll blame it on old age and drugs.. not the drugs you are thinking about..LOL