- Location
- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
I have a textbook example of not following code or having someone do the work that will. I'm working on a house and HO came to me with a problem unrelated to what I am doing. She is having a breaker trip when using her hairdryer. Turns out there is 2 bathrooms, a bedroom and a den/family room on one circuit. I checked the circuit with loads on that were said to be on when the breaker tripped. It is pulling 18-21A. I'm not sure if I had everything on but that was enough for me to see it was an overloading problem. I definitely need to pull at least 2 new circuits. The problem is the areas that need the circuits have no overhead space or crawl space since it is on a slab. Other than ripping stapled ceiling tile out or running cable in Wire Mold, anyone got any experienced, saged advise on how to run these new circuits? Any help would be appreciated.