At my facility we have a 3 phase 480v delta wye transformer( no neutral) feeding our plant with a high resistance ground package with an analog meter on it reading about 25 volts to ground. Measuring line to ground voltages on phase a is 283v, phase b 274v, phase c 295v. But measuring phase to phase I have roughly 480v +- 2 or 3 volts across all 3 phases. We have been having a few vfds and 480 to 24v power supplies going bad lately and I’m not sure if the phase to ground imbalance would cause that. I have had no luck tracing down the minor ground fault due to misreadings from the analog meter after isolating the 4 main switch gear breakers that it powers and also lack of down time. Is there a possibility that the meter needs to be recalibrated? Or could any one give advice on tracing down the ground fault with limited down time.