Fire alarm and maximum number of service disconnects

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
In NYC, if you have 6 service switches but you want to add another 7th service switch for fire alarm, are you allowed to do this?

Or are you stuck with maximum 6 service switches?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
2008 NEC:

230.72(B).
I don't see a problem in adding it but playing devil's advocate (Wayne may be an influence :) ) but 230.72(B) seemingly addresses a separate service situation. What if the F/A disconnect is added to an existing service ???
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't see a problem in adding it but playing devil's advocate (Wayne may be an influence :) ) but 230.72(B) seemingly addresses a separate service situation. What if the F/A disconnect is added to an existing service ???
It's additional disconnects for the things on the list that are over and above the up to 6 service disconnects of the same service.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It's additional disconnects for the things on the list that are over and above the up to 6 service disconnects of the same service.
Yep... Knew better than to question you :) I missed the "or" in the wording and thought it only applied to additional services
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yep... Knew better than to question you :) I missed the "or" in the wording and thought it only applied to additional services
Yeah it were an additional service we wouldn't need a rule {230.72(B)} for additional service disconnects for the same service.
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
2008 NEC:

230.72(B).
I'll take your word for it but I still don't understand that code reference...

What do they mean by "shall be installed remote from the one to six service disconnecting means for normal service".

Does "remote from" mean the additional service switch for fire alarm require to be in a different room?

and how does this "minimize the possibility of simultaneous interruption of supply"? that they claim
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'll take your word for it but I still don't understand that code reference...

What do they mean by "shall be installed remote from the one to six service disconnecting means".
They cannot be enclosed in the same switchboard as the other service disconnects. We typically use a separate disconnect switch.

IMG_20221212_095116360 (1).jpg
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
They cannot be enclosed in the same switchboard as the other service disconnects. We typically use a separate disconnect switch.

View attachment 2572105
Makes more sense thanks!

The funny thing is that 230.72(B) doesn't directly tell you that you are allowed to add fire alarm and fire pump service switches if you have already have existing 6 service switches, however they imply that it is permitted because they say "shall be installed remote from the one to six service disconnecting means"

If that makes sense lol
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Makes more sense thanks!

The funny thing is that 230.72(B) doesn't directly tell you that you are allowed to add fire alarm and fire pump service switches if you have already have existing 6 service switches, however they imply that it is permitted because they say "shall be installed remote from the one to six service disconnecting means"

If that makes sense lol
Yes the wording is not great but it does say "Additional Service Disconnecting Means". It's written as if there is some other section that mentions the fire pump/alarm service disconnects.
 

david

Senior Member
Location
Pennsylvania
I'll take your word for it but I still don't understand that code reference...

What do they mean by "shall be installed remote from the one to six service disconnecting means for normal service".
695.4 (B) (3)Disconnecting means.
Says a long with other things, located sufficiently remote from other building or other fire pump source Disconnecting means such that inadvertent operation at the same time would be unlikely.
Does "remote from" mean the additional service switch for fire alarm require to be in a different room?

and how does this "minimize the possibility of simultaneous interruption of supply"? that they claim
Also be aware of 695.3 (A) (1) a connection located ahead of and not within same cabinet, enclosure, ..... as the service disconnecting means

The conection located and arranged to minimize the the possibility of damage by fire
 