But where does it say that in the code? Thanks!No you can exceed 6 for things like fire pumps and fire alarm.
I don't see a problem in adding it but playing devil's advocate (Wayne may be an influence ) but 230.72(B) seemingly addresses a separate service situation. What if the F/A disconnect is added to an existing service ???2008 NEC:
230.72(B).
It's additional disconnects for the things on the list that are over and above the up to 6 service disconnects of the same service.I don't see a problem in adding it but playing devil's advocate (Wayne may be an influence ) but 230.72(B) seemingly addresses a separate service situation. What if the F/A disconnect is added to an existing service ???
Yep... Knew better than to question you I missed the "or" in the wording and thought it only applied to additional servicesIt's additional disconnects for the things on the list that are over and above the up to 6 service disconnects of the same service.
Yeah it were an additional service we wouldn't need a rule {230.72(B)} for additional service disconnects for the same service.Yep... Knew better than to question you I missed the "or" in the wording and thought it only applied to additional services
I'll take your word for it but I still don't understand that code reference...2008 NEC:
230.72(B).
They cannot be enclosed in the same switchboard as the other service disconnects. We typically use a separate disconnect switch.I'll take your word for it but I still don't understand that code reference...
What do they mean by "shall be installed remote from the one to six service disconnecting means".
Makes more sense thanks!They cannot be enclosed in the same switchboard as the other service disconnects. We typically use a separate disconnect switch.
View attachment 2572105
Yes the wording is not great but it does say "Additional Service Disconnecting Means". It's written as if there is some other section that mentions the fire pump/alarm service disconnects.Makes more sense thanks!
The funny thing is that 230.72(B) doesn't directly tell you that you are allowed to add fire alarm and fire pump service switches if you have already have existing 6 service switches, however they imply that it is permitted because they say "shall be installed remote from the one to six service disconnecting means"
If that makes sense lol
695.4 (B) (3)Disconnecting means.I'll take your word for it but I still don't understand that code reference...
What do they mean by "shall be installed remote from the one to six service disconnecting means for normal service".
Also be aware of 695.3 (A) (1) a connection located ahead of and not within same cabinet, enclosure, ..... as the service disconnecting meansDoes "remote from" mean the additional service switch for fire alarm require to be in a different room?
and how does this "minimize the possibility of simultaneous interruption of supply"? that they claim