hambone1216
Member
- Location
- Rochester new york
I went to a walk thru today to see about providing a price to run an annunciator from an existing FACP to a location in center of building. The building design is similar to a strip mall. Large shell broken up into smaller businesses.
I proposed running a conduit out of the riser room, from panel, to the exterior and continuing the raceway down building until I reach a common area where I can re-enter the building.
Fire alarm vendor told me that it is not permissible to run FA circuits outside building in any raceway.
the conduit would consist of 24volt power and signaling cable for parallel controls, is that still considered fire alarm circuits because it originates from FACP?
I cannot find anything code related in 760 that explains permissible or exclusions on either the exterior install or the prohibiting of.
Can you tell me where to look?
I proposed running a conduit out of the riser room, from panel, to the exterior and continuing the raceway down building until I reach a common area where I can re-enter the building.
Fire alarm vendor told me that it is not permissible to run FA circuits outside building in any raceway.
the conduit would consist of 24volt power and signaling cable for parallel controls, is that still considered fire alarm circuits because it originates from FACP?
I cannot find anything code related in 760 that explains permissible or exclusions on either the exterior install or the prohibiting of.
Can you tell me where to look?