C codequestion Banned Location MD, USA Jan 22, 2018 #1 Does NEC 2014 have any article in Fire systems Article 760 or elsewhere regarding Fire Alarm Annunciator Panel? Location wiring etc etc.
Does NEC 2014 have any article in Fire systems Article 760 or elsewhere regarding Fire Alarm Annunciator Panel? Location wiring etc etc.
gadfly56 Senior Member Location New Jersey Occupation Professional Engineer, Fire & Life Safety Jan 22, 2018 #2 codequestion said: Does NEC 2014 have any article in Fire systems Article 760 or elsewhere regarding Fire Alarm Annunciator Panel? Location wiring etc etc. Click to expand... No. Annunciator location, if required, will be in NFPA 72: 10.18.3.2 All required annunciation means shall be located as required by the authority having jurisdiction to facilitate an efficient response to the situation. The above is from the 2013 edition.
codequestion said: Does NEC 2014 have any article in Fire systems Article 760 or elsewhere regarding Fire Alarm Annunciator Panel? Location wiring etc etc. Click to expand... No. Annunciator location, if required, will be in NFPA 72: 10.18.3.2 All required annunciation means shall be located as required by the authority having jurisdiction to facilitate an efficient response to the situation. The above is from the 2013 edition.
luckylerado Senior Member Location Lake of the Ozarks Jan 23, 2018 #3 Wiring varies based on type and manufacture. You will need product data to know what to pull to the backbox.
Wiring varies based on type and manufacture. You will need product data to know what to pull to the backbox.