Fire alarm bell 14/2 isolated

JJWalecka

Senior Member
Location
New England
If you could look at the image you will see the EMT feeding 120 to the fire alarm panel goes through the trough.

My question is the 14/2 that goes out to feed the "bell"....does that also need to be isolated from all the fire alarm cables in the trough. Thanks
 

Attachments

  • IMG_20240928_104513.jpg
    IMG_20240928_104513.jpg
    952.6 KB · Views: 5

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If the fire alarm system is a power limited system, (not even sure if they make non-power limited fire alarm systems anymore, then the 120 volt bell circuit will need to be isolated from the power limited fire alarm cables. 760.136.
 