C connectjim Member Oct 17, 2006 #1 When you install fire alarm cables (Type FPL or NPLF) in conduits run vertically do you have to follow 300.19 for vertical supports? Jim
When you install fire alarm cables (Type FPL or NPLF) in conduits run vertically do you have to follow 300.19 for vertical supports? Jim
O orgonfire Member Location Portland, OR Oct 31, 2006 #2 300.19 only refers to conductors run in a vertical 'raceway'.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 1, 2006 #3 300.19 does not apply to fire alarm cables. See 760.3. Don