D deharoj Member Mar 31, 2006 #1 Is there anything in the code that requires a dedicated cicuit? We usually give a dedicated circuit, however we do this as a precaution and a safety measure so that it won't trip.
Is there anything in the code that requires a dedicated cicuit? We usually give a dedicated circuit, however we do this as a precaution and a safety measure so that it won't trip.
J jtester Senior Member Location Las Cruces N.M. Mar 31, 2006 #3 I don't have access to my fire codes today, but I bet it is a requirement of various fire codes. Jim T
I don't have access to my fire codes today, but I bet it is a requirement of various fire codes. Jim T
bdarnell Senior Member Location Indianapolis, IN Occupation Retired Engineer Mar 31, 2006 #4 NFPA 72 1-5.2.5.2 requires a dedicated circuit when light and power sources are used to provide primary power.
NFPA 72 1-5.2.5.2 requires a dedicated circuit when light and power sources are used to provide primary power.